My model requires glass doors, but my attempt to use a window construction for the door results in a sever error because it energy plus will not recognize the window construction materials in a "door" fenestration construction .

Is there a way to model the glass door as a door or is it ok to lable the door as a window?

As a work around, I thought I could rename the door surface as a window (by leaving 1/2" of wall surface at the bottom of the "window"). I assume that since the material is the dominant feature of the surface, this would be acceptable.

Interested in any feedback for the best way to approach creating a glass door in Euclid/EnergyPlus.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
4

answered 2018-02-12 04:25:55 -0600

There are 2 ways to model subsurfaces in E+: simplified and detailed. For the detailed mode you will use the FenestrationSurface:Detailed object (regardless if you are modelling windows, doors or glazed doors). In this case the subsurface is defined geometrically, through the coordinates of each vertex. In the simplified mode you will have a different object, depending on the subsurface type (window, door, glazed door,...). You will input it through few geometrical information and you will be only able to model rectangular subsurfaces. In both cases you will be able to assign constructions, shading, frame, etc to your subsurface.

As default, Euclid will input your subsurface in the detailed mode. If this is the object you are using, then you should check the "Surface type" field and be sure to set it to "GlassDoor". Then it will allow you to use transparent materials. If you use the "Door" type, you can only assign opaque materials to it. However, you will find detailed information about it in the InputOutputReference.

If you are interested in other ways to model windows or glass doors in EnergyPlus, you should have a look at the WINDOW program, that allows you to model your windows and then export them as E+ objects (here).