Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Design Load With Sizing Factor

asked 2018-02-08 22:04:12 -0600

FN's avatar

updated 2018-03-11 10:51:59 -0600

How should we use "the sizing factor"? Typically the cooling load calculated by OS is very low, is the default cooling sizing factor of 1.15 based on comparison with Trace 700?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2018-02-09 04:41:16 -0600

Gio's avatar

ASHRAE appendix G says: The equipment capacities for the baseline building design shall be based on sizing runs for each orientation (per Table G3.1, No. 5a) and shall be oversized by 15% for cooling and 25% for heating, i.e., the ratio between the capacities used in the annual simulations and the capacities determined by the sizing runs shall be 1.15 for cooling and 1.25 for heating.

If you oversize more than 1.15 your chiller would work with a lower EER most of the time.

edit flag offensive delete link more

Comments

Thank you Gio, it makes sense. I noticed the factor can be chosen by the user of OS and when I read a few old old/conversations here I misunderstood this factor has been added to make up the difference between the calculated loads from Trace 700 and OS! I don't know if there is any update Re this difference or not!

FN's avatar FN  ( 2018-02-09 08:19:15 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2018-02-08 22:04:12 -0600

Seen: 283 times

Last updated: Feb 09 '18