Plant loop is not operated

asked 2018-01-25 03:05:06 -0600

katsuya.obara's avatar

updated 2018-01-25 07:32:26 -0600

I am modelling VAV system with water cooled chiller using OpenStudio 2.4.
Even though I modeled HVAC sytstem (and didnt get error), cooling/heating setpoint, Hours of operation in Schedule Sets, Availability schedule for cooling coil, energy simulation result doesnt consume any energy for cooling. (Fan is operating). From my experience, these are the setting I was checking.
Does anyone know what I should check further to solve this problem?

edit retag flag offensive close merge delete

Comments

Can you post more information on your inputs or link to your model?

mdahlhausen's avatar mdahlhausen  ( 2018-01-25 15:03:28 -0600 )edit

@mdahlhausen Thank you for your reply. I uploaded file to google drive. please find the file from this link

katsuya.obara's avatar katsuya.obara  ( 2018-01-25 18:15:51 -0600 )edit

do you have an .osm file? that'll make it easier to find the error.

mdahlhausen's avatar mdahlhausen  ( 2018-01-25 19:14:18 -0600 )edit

1 Answer

Sort by ยป oldest newest most voted
2

answered 2018-01-25 22:14:26 -0600

katsuya.obara's avatar

I could figure out the problem.
Problem existed in Sizing:Plant
I forgot to change Design Loop Exit Temperature which was 82 deg as default for chiller plant loop.

edit flag offensive delete link more