Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
4

How to model air free cooling in openstudio?

asked 2018-01-22 08:04:42 -0500

Mans_sopers's avatar

I'm not really familiair with all the HVAC options and I'm not sure what settings should be set manually or autoscaled. I'm trying to model a micro data room which uses direct air free cooling. Heating is currently done with an electric coil heater. Could anyone help me with how to model this?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
4

answered 2018-01-22 16:14:57 -0500

updated 2018-01-22 16:52:40 -0500

Since this is a data room, I'm going to assume that by "free cooling" you mean it has an economizer, and not that it uses natural ventilation. You could start with an HVACTemplate- maybe a Unitary system depending on what you are looking for. If you have no DX cooling, you can specify the cooling coil type as "none", but still specify economizer operation. Reference the HVACTemplate-5ZoneUnitarySystemin the "ExampleFiles" folder of your EnergyPlus installation.

Or you could look at the "2ZoneDataCenterHVAC_wEconomizer" example file.

edit flag offensive delete link more

Comments

1

The type of cooling I'm referring to is this one https://www.systemair.com/na/north-am..., except that it's attached to a wall directly located in the data room. The data room is relatively small, I'm talking about 10-20 towers. How do I reference to one of the systems from EnergyPlus?

Thanks for your reply and consideration.

Mans_sopers's avatar Mans_sopers  ( 2018-01-24 03:25:54 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2018-01-22 08:04:42 -0500

Seen: 455 times

Last updated: Jan 22 '18