Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

Why is there no heat rejection energy from air cooled VRF?

asked 2018-01-16 17:59:03 -0500

CRHavis's avatar

updated 2018-01-17 22:10:18 -0500

bbrannon4's avatar

Is it always included in the (air cooled) compressor energy?

There is cooling energy, but I would expect to see some condenser fan energy under heat rejection. I did not see any way to connect condenser fans, so I assume that the assumption was the condenser fan energy is always rolled up with the compressor.

Openstudio 2.3.0

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
5

answered 2018-01-17 12:41:00 -0500

In EnergyPlus, compressor energy for air-cooled AirConditioner:VariableRefrigerantFlow objects are included under Cooling:Electricity, not HeatRejection:Electricity. You can look at the .mtd output file to see which equipment is included on which meters.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2018-01-16 17:59:03 -0500

Seen: 136 times

Last updated: Jan 17 '18