zone control thermostat - cooling autosize doesn't work
I have made an energyplus model, When I see the ESO "Zone Mean Air Temperature", the cooling schedule doesn't seems work, so I'm not sure the result is correct or not. please see result below:
my setting is like below:
Schedule:Compact,
Htg-SetP-Sch, !- Name
Temperature, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Saturday Sunday Holiday SpecialDays, !- Field 2
Until: 24:00, !- Field 3
5, !- Field 4
For: AllOtherDays, !- Field 5
Until: 7:00, !- Field 6
5, !- Field 7
Until: 8:00, !- Field 8
14, !- Field 9
Until: 18:00, !- Field 10
20, !- Field 11
Until: 24:00, !- Field 12
5; !- Field 13
Schedule:Compact,
Clg-SetP-Sch, !- Name
Temperature, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Saturday Sunday Holiday SpecialDays, !- Field 2
Until: 24:00, !- Field 3
40, !- Field 4
For: AllOtherDays, !- Field 5
Until: 7:00, !- Field 6
40, !- Field 7
Until: 8:00, !- Field 8
30, !- Field 9
Until: 18:00, !- Field 10
25.0, !- Field 11
Until: 24:00, !- Field 12
40; !- Field 13
Schedule:Compact,
Zone Control Type Sched, !- Name
Control Type, !- Schedule Type Limits Name
Through: 03/30, !- Field 1
For: AllDays, !- Field 2
Until: 24:00, !- Field 3
1, !- Field 4
Through: 05/30, !- Field 5
For: AllDays, !- Field 6
Until: 24:00, !- Field 7
4, !- Field 8
Through: 10/16, !- Field 9
For: AllDays, !- Field 10
Until: 24:00, !- Field 11
2, !- Field 12
Through: 11/30, !- Field 13
For: AllDays, !- Field 14
Until: 24:00, !- Field 15
4, !- Field 16
Through: 12/31, !- Field 17
For: AllDays, !- Field 18
Until: 24:00, !- Field 19
1; !- Field 20
What do you mean "the cooling schedule doesn't seem to work"? From the graph you supplied, it's hard to tell if there's anything wrong, if you could zoom in and point an area where you think it's not ok, that'll help... I also have no idea what's the red crosses versus the blue line since there's no legend.