VAV system with constant air flow rate(EnergyPlus)

asked 2017-12-18 11:45:34 -0600

joooon's avatar

updated 2017-12-19 11:35:10 -0600

Hi! now i am running a VAV system with EnergyPlus.

i just found that the supply air is supplied in same flow rate constantly specially in summer.

but it is weird that air supply flow rate changes variably in winter and spring

what in this case, objects should i check for variable flow rates?

edit retag flag offensive close merge delete

Comments

Could you provide more information on your system such as air handler objects and terminal unit types, and any schedules related to your fan objects?

kramerica's avatar kramerica  ( 2017-12-19 13:47:35 -0600 )edit

1 Answer

Sort by ยป oldest newest most voted
1

answered 2017-12-19 13:52:46 -0600

Check your air handler fan objects types and if Fan:VariableVolume its max and min values, terminal units, sizing:system field central heating maximum system airflow ratio, and sizing:zone field heating max airflow fraction.