Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

VAV system with constant air flow rate(EnergyPlus)

asked 2017-12-18 11:45:34 -0500

joooon's avatar

updated 2017-12-19 11:35:10 -0500

Hi! now i am running a VAV system with EnergyPlus.

i just found that the supply air is supplied in same flow rate constantly specially in summer.

but it is weird that air supply flow rate changes variably in winter and spring

what in this case, objects should i check for variable flow rates?

edit retag flag offensive close merge delete

Comments

Could you provide more information on your system such as air handler objects and terminal unit types, and any schedules related to your fan objects?

kramerica's avatar kramerica  ( 2017-12-19 13:47:35 -0500 )edit

1 Answer

Sort by ยป oldest newest most voted
1

answered 2017-12-19 13:52:46 -0500

Check your air handler fan objects types and if Fan:VariableVolume its max and min values, terminal units, sizing:system field central heating maximum system airflow ratio, and sizing:zone field heating max airflow fraction.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2017-12-18 11:45:34 -0500

Seen: 214 times

Last updated: Dec 19 '17