Report ASHRAE 62.1 with single zone system in openstudio

asked 2017-11-15 13:04:18 -0500

dalin_si's avatar

updated 2020-01-27 18:42:09 -0500

Hi All,

I want to export the report about Report ASHRAE 62.1 from openstudio model, but I notice that the report only can show the AHU, so how about the single zone system with only one supply fan? how to make them shown on ASHRAE 62.1 report?

thanks

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2018-01-18 02:44:10 -0500

ASHRAE 62.1 calculations for a single zone system will be very simple and straightforward, but are still presented at the system level. The goal of the calculation is to determine the outside air intake at the system level, which for a single zone system is equal to Vbz/Ez (breathing zone outdoor airflow divided by the zone distribution effectiveness).

If you have a Controller:MechanicalVentilation specified you should get the ASHRAE 62.1 report to populate.