Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

How to output heating gains/losses from zone ventilation in the Airflow Network

asked 2017-10-02 18:18:01 -0600

saeranv's avatar

I have modeled a naturally ventilated multi-zone structure in EnergyPlus using the AIrflow Network. I've been trying to output the heating gains/losses due to ventilation, however that output-variable doesn't seem to exist in the Airflow Network Outputs. Curiously, the sensible and latent heat gain/loss from zone infiltration, and zone mixing from the AFN exists, but not ventilation...

Is there a reason why this is not provided? And is there another output-variable I can use to calculate this i.e. using the AFN Linkage Node 1 to 2 Average Mass Flow Rate and outdoor and zone temperatures to manually calculate ventilation heat loss/gain myself?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2017-10-05 23:11:22 -0600

saeranv's avatar

I think I've found the answer here. Somewhat confusingly, the AFN Zone Infiltration output is the sum of ventilation and crack flows into the zone.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2017-10-02 18:18:01 -0600

Seen: 4,215 times

Last updated: Oct 05 '17