Control of PTHP and WaterToAirHeatPump

asked 7 years ago

updated 7 years ago

I have one building with two design options. One applies air source heat pump (simulated as ZoneHVAC:PackagedTerminalHeatPump); the other uses water source heat pump (simulated as ZoneHVAC:WaterToAirHeatPump). Results show WSHP has much more heating than ASHP which seems not reasonable to me. I checked the hourly report and found for ASHP case, heating coil (Coil:Heating:DX:SingleSpeed) did not run at the same time with supplemental electric heating; while in WSHP case, heating coil (Coil:Heating:WaterToAirHeatPump:EquationFit) often run at the same time with supplemental coil. Any control difference between ASHP and WSHP units?

Preview: (hide)

Comments

What does the comparison of outside air rates tell you?

TomB's avatar TomB  ( 7 years ago )

2 Answers

Sort by » oldest newest most voted
1

answered 7 years ago

The DX heating coil will not operate below the Minimum Outdoor Air Temperature for Compressor Operation while the water-source heating coil will. Check the min OAT for compressor operation and compare to the weather file outdoor temperature.

Preview: (hide)
link

Comments

@rraustad, thanks for your advice. I checked the control, it does have some influence, but not too much. I use the same building for two cases, but when I checked the heating coil heating rate, WSHP case will have 30-50% more heating rate than ASHP. To my understanding, same building means same load which will bring similar heating rate, is that correct? Why WSHP have much more energy consumption than ASHP? (WSHP even have higher COP)

Yan's avatar Yan  ( 7 years ago )

What is the DX heating coil's Minimum OAT for Compressor Operation and what is the weather file outdoor temperature when the DX heating coil does not run and the WSHP heating coil does run?

rraustad's avatar rraustad  ( 7 years ago )

@Yan, your correct that the heating loads should be the same. When you add the DX heating coil rate + supplemental heating coil rate and compare that to WSHP heating coil rate + supplemental heating coil rate are these the same? Is WSHP heating coil rate + supplemental heating coil rate still higher than the total heating coil rate from the ASHP?

rraustad's avatar rraustad  ( 7 years ago )

@rraustad, the minimum OAT for compressor is 17.6F, and supplemental electric DX heating coil does not run when the DX heating coil runs, this situation happens at most time of the year, anytime of the day, seems not that related with OAT. WSHP supplemental coil, however, run much more than ASHP supplemental coil, usually in early morning

Yan's avatar Yan  ( 7 years ago )

@rraustat, yes, when I compare the sum of DX heating coil rate + supplemental coil rate, WSHP higher than ASHP, if the load is the same, what could cause the different heating rates?

Yan's avatar Yan  ( 7 years ago )
1

answered Jan 26

Greg Estep's avatar

updated Jan 26

I realize this is an old post, but I have issues when autosizing ZoneHVAC:PackagedTerminalHeatPump) and ZoneHVAC:WaterToAirHeatPump.

I often make this comparison and found that the PTHP is autosized as expected while the ZoneHVAC:WaterToAirHeatPump is significantly oversized.

Further, when hard sizing the ZoneHVAC:WaterToAirHeatPump, the coil peak maximum cooling rate never reaches capacity, only about 50%.

I use DesignBuilder which is still using E+ v9.4.

Any comments from others would be appreciated.