the difference between **Fan Coil Total Cooling Rate** and **Cooling Coil Total Cooling Rate**?

asked 2017-08-21 01:10:31 -0600

Richard's avatar

updated 2017-08-21 08:38:39 -0600

What is the difference between Fan Coil Total Cooling Rate and Cooling Coil Total Cooling Rate? I put ZoneHVAC:FourPipeFanCoil in a zone,and i found huge difference between Fan Coil Total Cooling Rate and Cooling Coil Total Cooling Rate, the Cooling Coil Total Cooling Rate is much larger than Fan Coil Total Cooling Rate, why?

edit retag flag offensive close merge delete

2 Answers

Sort by » oldest newest most voted
4

answered 2017-08-21 08:33:35 -0600

Because of outdoor air. The Fan Coil Total Cooling Rate is what is provided to the zone (i.e., Tsa - Tzone). The Cooling Coil Total Cooling Rate is the total load on the system coil including fan heat and outdoor air load (i.e., Tcoil, outlet - Tcoil, inlet).

edit flag offensive delete link more
1

answered 2017-08-21 19:47:43 -0600

Richard's avatar

updated 2017-08-22 19:06:13 -0600

Another description for this topic:

The Fan Coil Total Cooling Rate is about the condition between R.A. and S.A.

The Cooling Coil Total Cooling Rate is about the condition between M.A.(R.A.+O.A.) and S.A. (including fan heat)

edit flag offensive delete link more

Comments

1

M.A. also includes outdoor air load if OA is part of the simulation.

rraustad's avatar rraustad  ( 2017-08-22 07:38:31 -0600 )edit