Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

Heating and Cooling Schedules based on Outdoor Temperature

asked 2017-07-07 12:21:53 -0500

map1995's avatar

updated 2017-07-07 19:46:18 -0500

Using DesignBuilder software... I am wondering if there is a way to set the schedules for the heating and cooling systems to be based on outdoor air temperature? For example, for chilled water loop availability schedule, I want it to turn on when it is warmer than 54 degrees F.

Is there a way to do this with the DesignBuilder compact schedules?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2017-07-09 17:27:03 -0500

Compact schedules are only able to set values according to time (minute, hour, day, etc.) throughout the simulation. To force the chilled water system to be available when outdoor air dry-bulb is above 54F, then within DesignBuilder you want to do the following:

  1. In detailed HVAC mode, click on the chilled water loop
  2. Click on "Edit loop data"
  3. Check the box for "Outside temperature operation"
  4. Set "External cut-in temperature" to 54F

If you want to apply an external cut-out temperature below which the chilled water system is forced off, then you could use the "External cut-out temperature" field to do so. These inputs both override the normal availability schedule assigned to the chilled water loop. That means that if the outdoor air temperature is at or above cut-in, the system is available regardless of availability schedule, and if the outdoor air temperature is at or below cut-out, the system is forced off regardless of availability schedule. If the outdoor air temperature is between cut-in and cut-out, then availability schedule values are used.

Refer to the screen shot below as well as the Outside temperature operation section of the Plant And Condenser Loop Edit Dialog DesignBuilder help documentation.

image description

Setting external cut-in temperature for chilled water loop in DesignBuilder

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2017-07-07 12:21:53 -0500

Seen: 1,838 times

Last updated: Jul 09 '17