Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

How can I confirm that my model is working properly?

asked 2017-06-21 09:00:42 -0500

sirYESsir's avatar

updated 2017-06-26 15:49:09 -0500

I was given a model that was fully operational.

So I removed the whole functional, yet obsolete, HVAC system and inserted a new one with ideal loads, for I need to know what are the exact loads that the building is experiencing and refurbish the envelope accordingly.

The thing now is that, after running my new model and comparing it with the former one, I seem to have loads that are around 4 to 7 times higher for each zone.

I mean, the former HVAC system was really poorly designed, but THAT poorly? It is also known that the building's envelope is terrible when it comes to thermal insulation.

Or is it likely that my new model isn't running properly?

edit retag flag offensive close merge delete

Comments

1

What do you mean by "loads"? Do you mean the total heating energy for the year? Or the Peak Heating rate?

Julien Marrec's avatar Julien Marrec  ( 2017-06-26 15:53:46 -0500 )edit

I was referring to the total heating energy.

I also solved my problem already. It seems like I was comparing the sensible heating energy of the initial problem with the total heating energy of my new model, which included the internal gains.

So instead of having 4 to 7 times difference, I have 2 to 3 now. Solved!

sirYESsir's avatar sirYESsir  ( 2017-07-05 09:50:28 -0500 )edit

1 Answer

Sort by ยป oldest newest most voted
4

answered 2017-06-21 09:16:10 -0500

The original system likely had unmet hours - periods of time where the setpoint wasn't achieved. The ideal loads case will always meet setpoints resulting in higher heating or cooling loads. 4-7x more seems excessive, but checking how far off setpoint the original model was will tell you if that's legit.

edit flag offensive delete link more

Comments

Thank you for your answer, Ljbrackney.

In fact, my ideal system is having 1200 hours not met, against 4000 of the original one (out of 1 year).

  • Is this difference big enough to justify the differences in loads?
  • And is it normal that my ideal system is having unmet hours?
sirYESsir's avatar sirYESsir  ( 2017-06-21 09:26:27 -0500 )edit
1

So 4x unmet hours - that could translate to the kind of load variation you're seeing. One of the E+ guys can chime in on your ideal air load unmet hours. My understanding is that ideal air loads should achieve setpoints with as much district heating or cooling as is needed, but I could be wrong.

ljbrackney's avatar ljbrackney  ( 2017-06-21 09:47:09 -0500 )edit
1

Contrary to OpenStudio where the idealLoads is a checkbox, the EnergyPlus ZoneHVAC:IdealLoadsAirSystem can be customized quite heavily, including input for the heating/cooling limiting values, availability schedules for heating/cooling, etc. All of which can easily lead to 1000 unmet hours.

Julien Marrec's avatar Julien Marrec  ( 2017-06-26 15:52:56 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2017-06-21 09:00:42 -0500

Seen: 196 times

Last updated: Jun 26 '17