Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
4

What if autosizing produces unmet hours for the design days ?

asked 2017-06-19 08:45:35 -0500

updated 2017-06-23 07:55:10 -0500

I have set up an OS model with complete autosizing for 7 design days. I would like to achieve zero unmet hours for the design days. However, when increasing heating and cooling capacities manually, there seems to be little effect or even convergence problems during warming-up. Also the OS unmethours troubleshooting reporting measure failed, i.e. crashed.

What's your advice ?

edit retag flag offensive close merge delete

2 Answers

Sort by ยป oldest newest most voted
2

answered 2017-08-11 11:34:47 -0500

HOW TO ACHIEVE ZERO UNMET HOURS

(1) COMPLETENESS After discovering that not all HVAC components had been installed yet and adding missing components, amount of unmet hours was reduced.

(2) CONSISTENCY temperature setpoints, and temperature schedules must be consistent, and temperature differences between in- and outflows must be adequate to enable the system to provide sufficient heating and cooling power.

(3) VOLATILITY AND INERTIA Source of highly dynamic change may be solar radiation, or EMS controls, while the building and the HVAC system may react with inertia. Performance can be improved e.g. by dynamic shading to avoid extremes from solar radiation gains, by switching to dynamic (EMS controlled) natural ventilation (infiltration), and by programming EMS controls with hystereses in the ON-OFF criteria.

(4) CONVERGENCE AND ERRORS convergence problems (e.g. due to highly dynamic changes in some zones or HVAC components) may lead to increased unmet hours results, which partly may be eliminated by steps under paragraph (3). In one case it was possible to eliminate a convergence problem by increasing thermal mass of affected zone(s) by cross-mixing, which anyway were not truely separated in reality, (in EnergyPlus separated only by "air wall") but together constituted a non-convex thermal zone. Checking (severe) error messages may also help to improve performance.

(5) NECESSITY It was found that not for all zones the same heating and cooling setpoints need to apply. Relaxing e.g. the cooling setpoint for a bathroom (which essentially did not need cooling), finally produced the desired result: ZERO unmet hours during occupied hours.

image description

edit flag offensive delete link more
1

answered 2017-06-21 18:08:00 -0500

BilalMaarouf's avatar

Trying changing the supply air flow rate, the setpoint schedule, and marginally increase the reheat delta T (if any). One of those should reduce the unmet hours.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

2 followers

Stats

Asked: 2017-06-19 08:45:35 -0500

Seen: 474 times

Last updated: Aug 11 '17