temperature control;Tolerance temperature

asked 2017-05-21 08:33:01 -0600

Done's avatar

updated 2017-05-22 07:30:27 -0600

I want to know how can I set the "Tolerance temperature" in E+ which is the temperature control. The situation can be describe that I want to use AC when the room temperature is higher than 29 ℃,but if I use AC the cooling setpoint is 26 ℃.

So which temperature should I fill in HVAC Templates:Themostat Constant Cooling Setpoint ? And if I can set the two schedule to meet the situation that when the room temperature lower than 29 ℃ I close the AC although the operation schedule is on.

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
2

answered 2017-05-22 06:15:53 -0600

Could have been helpful to share what type of AC system you plan on using, but either way I think you can do the following:

This would look like the following, making sure you replace the 'Sensor Node' by a valid Outside Air node

AvailabilityManager:HighTemperatureTurnOn,
  AC HighTemp Turn On Availability Manager,   !- Name
  Outside Air Inlet Node,   !- Sensor Node
  29.0;   !- Temperature {C}
edit flag offensive delete link more

Comments

Thank You for your answer.Now I want to set EMS contorl with IdealLoadAirSystem.The sensor is one zone's mean air temperature and the actuator that I want to contorl the zone's operation schedule on or off. It always occur error " * Severe * Invalid Actuated Component Unique Name =18B11"
EnergyManagementSystem:Sensor ,ZoneRT , !- Name;18B11, !- Output:Variable Index Key Name Zone Operative Temperature; ! EnergyManagementSystem:Actuator ,MyOpenFactor , !- Name;Bedroom operation, !- Actuated Component Unique Name;Schedules, !- Actuated Component Type;Schedule Value; !- Actuated Component

Done's avatar Done  ( 2017-05-24 08:37:25 -0600 )edit

This should be a separate question. Also, if this answer solved your problem, please mark it as accepted so we can flag the thread as resolved.

Julien Marrec's avatar Julien Marrec  ( 2017-05-24 10:48:22 -0600 )edit

That is my falut and I start the new question. Thank you and I hope you can give me some advides.