Hi , I'm using Openstudio 2.1 ,I've applied OpenStudio Result to reporting measures , when I run the simulation I get the following error with no result. Failed: IP units were provided, SI units were expected. Leave EnergyPlus tabular results in SI units to run this report.

I need both Energy plus and OpenStudio reports to get End uses and monthly utility rate.Thanks.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2017-04-19 09:48:53 -0600

Tim Johnson's avatar

I have had this issue before as well. From what I understand, OpenStudio counts on converting the EnergyPlus results from SI to IP. My guess is you are running the measure "Set Output Table to IP Units." If you delete that measure, the OpenStudio results should work.

There is a little more explanation from David Goldwasser here: https://unmethours.com/question/20371....

edit flag offensive delete link more

Comments

Thank so much Tim. It worked.

Salaviza's avatar Salaviza  ( 2017-04-19 22:45:28 -0600 )edit