Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Error when I apply OpenStudio Result in Reporting measures.

asked 2017-04-18 16:06:57 -0500

Salaviza's avatar

Hi , I'm using Openstudio 2.1 ,I've applied OpenStudio Result to reporting measures , when I run the simulation I get the following error with no result. Failed: IP units were provided, SI units were expected. Leave EnergyPlus tabular results in SI units to run this report.

I need both Energy plus and OpenStudio reports to get End uses and monthly utility rate.Thanks.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2017-04-19 09:48:53 -0500

Tim Johnson's avatar

I have had this issue before as well. From what I understand, OpenStudio counts on converting the EnergyPlus results from SI to IP. My guess is you are running the measure "Set Output Table to IP Units." If you delete that measure, the OpenStudio results should work.

There is a little more explanation from David Goldwasser here: https://unmethours.com/question/20371....

edit flag offensive delete link more

Comments

Thank so much Tim. It worked.

Salaviza's avatar Salaviza  ( 2017-04-19 22:45:28 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2017-04-18 14:06:34 -0500

Seen: 409 times

Last updated: Apr 19 '17