Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Heating and Cooling setpoint temperatures on Design Builder

asked 2017-04-17 22:43:06 -0500

Jéssicamarasantos's avatar

updated 2017-04-18 07:33:09 -0500

Hi!

I would like to switch on my cooling and heating systems when the operative temperature is out of the range of comfortable temperatures (i.g from 20°C to 28°C). Is it possible to set the setpoint temperatures so that the heating will be required when the zone temperature is lower than 20°C and the cooling will be required when the zone temperature is higher than 28°C ?

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
1

answered 2017-04-18 00:57:37 -0500

banicu's avatar

In the Activity tab set the Heating setpoint at 20C and the Cooling setpoint at 28C. Then enter in the Simulation tab, Options and select Operative temperature control. image description

edit flag offensive delete link more

Comments

Thank you for the shotscreens

Jéssicamarasantos's avatar Jéssicamarasantos  ( 2017-04-18 09:29:03 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

Stats

Asked: 2017-04-17 22:43:06 -0500

Seen: 3,063 times

Last updated: Apr 18 '17