Heating and Cooling setpoint temperatures on Design Builder

asked 7 years ago

Jéssicamarasantos's avatar

updated 7 years ago

Hi!

I would like to switch on my cooling and heating systems when the operative temperature is out of the range of comfortable temperatures (i.g from 20°C to 28°C). Is it possible to set the setpoint temperatures so that the heating will be required when the zone temperature is lower than 20°C and the cooling will be required when the zone temperature is higher than 28°C ?

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
1

answered 7 years ago

banicu's avatar

In the Activity tab set the Heating setpoint at 20C and the Cooling setpoint at 28C. Then enter in the Simulation tab, Options and select Operative temperature control. image description

Preview: (hide)
link

Comments

Thank you for the shotscreens

Jéssicamarasantos's avatar Jéssicamarasantos  ( 7 years ago )