Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Heating and Cooling setpoint temperatures on Design Builder

asked 2017-04-17 22:43:06 -0600

Jéssicamarasantos's avatar

updated 2017-04-18 07:33:09 -0600

Hi!

I would like to switch on my cooling and heating systems when the operative temperature is out of the range of comfortable temperatures (i.g from 20°C to 28°C). Is it possible to set the setpoint temperatures so that the heating will be required when the zone temperature is lower than 20°C and the cooling will be required when the zone temperature is higher than 28°C ?

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
1

answered 2017-04-18 00:57:37 -0600

banicu's avatar

In the Activity tab set the Heating setpoint at 20C and the Cooling setpoint at 28C. Then enter in the Simulation tab, Options and select Operative temperature control. image description

edit flag offensive delete link more

Comments

Thank you for the shotscreens

Jéssicamarasantos's avatar Jéssicamarasantos  ( 2017-04-18 09:29:03 -0600 )edit