Where can I set my zones relative humidity in Open Studio?

asked 2017-04-10 13:15:46 -0600

Nail Rachidi's avatar

updated 2017-04-13 13:49:58 -0600

I specified my RH under my thermal zones but it seems that my simulation results are not taking that into consideration. Most of my thermal zones spend most of there hours with RH<30% Even though i set max: 60% and min:40%

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2017-04-10 14:15:53 -0600

The thermal zone is where you define what you want the zone RH to be, but that doesn't mean the systems that affect zone RH know to control humidity in those zones. For that, you need additional input. I've described the required input for a chilled-water air loop system here. The idea will be generally the same for other air loop-based systems; for other system or component types I recommend reading the Input/Output Reference.