Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
0

Where can I set my zones relative humidity in Open Studio?

asked 2017-04-10 13:15:46 -0500

Nail Rachidi's avatar

updated 2017-04-13 13:49:58 -0500

I specified my RH under my thermal zones but it seems that my simulation results are not taking that into consideration. Most of my thermal zones spend most of there hours with RH<30% Even though i set max: 60% and min:40%

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2017-04-10 14:15:53 -0500

The thermal zone is where you define what you want the zone RH to be, but that doesn't mean the systems that affect zone RH know to control humidity in those zones. For that, you need additional input. I've described the required input for a chilled-water air loop system here. The idea will be generally the same for other air loop-based systems; for other system or component types I recommend reading the Input/Output Reference.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2017-04-10 13:15:46 -0500

Seen: 321 times

Last updated: Apr 10 '17