Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

How to automatically size chiller equally ?

asked 2017-03-21 13:31:41 -0600

BL's avatar

updated 2017-08-07 13:22:40 -0600

I found out that the calculated size of chiller is the same for having one chiller in the loop or two, or three or even more. Is it possible to let the OS automatically split the chiller size equally ?

Or has it to be done by hard size ? (e.g size of one chiller / number of chillers)

Thank you

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
5

answered 2017-03-21 13:50:40 -0600

The 'Sizing Factor' field in your chiller object can be used to distribute the peak load between autosized components.

image description

If you have two chillers and you would like them to be sized equally, enter '0.5' as the sizing factor for each chiller.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2017-03-21 13:31:41 -0600

Seen: 184 times

Last updated: Mar 21 '17