How to automatically size chiller equally ?

asked 2017-03-21 13:31:41 -0500

BL's avatar

updated 2017-08-07 13:22:40 -0500

I found out that the calculated size of chiller is the same for having one chiller in the loop or two, or three or even more. Is it possible to let the OS automatically split the chiller size equally ?

Or has it to be done by hard size ? (e.g size of one chiller / number of chillers)

Thank you

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
5

answered 2017-03-21 13:50:40 -0500

The 'Sizing Factor' field in your chiller object can be used to distribute the peak load between autosized components.

image description

If you have two chillers and you would like them to be sized equally, enter '0.5' as the sizing factor for each chiller.