Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

Discrepancy in Coil size in HTML vs Coil size in eso hourly profile

asked 2017-03-21 12:14:07 -0500

updated 2017-05-08 15:42:15 -0500

Hello All,

Why the chiller coil sizing in HTML is higher ( approx. 30-40%) than the coil size reported under eso variable hourly output. Similar, behavior has been observed for the the zone cooling coil load reported under HTML and .eso hourly output profile. The hourly coil load never touches the value reported in HTML.

Any insight would be highly appreciated.

Thanks,

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2017-03-21 15:02:14 -0500

It may be because of Sizing:Parameters Cooling Sizing Factor. I think the default value is 1, but maybe it is 1.3 in your idf.

edit flag offensive delete link more

Comments

Thank you, Adam. Yes, this was one of the reason as DB uses sizing factor at different locations and i missed out somewhere.

Thanks again!!

Javed's avatar Javed  ( 2017-04-24 08:55:53 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2017-03-21 12:14:07 -0500

Seen: 101 times

Last updated: Mar 21 '17