No HVAC Energy Used in Simulation
EnergyPlus v8.5
System7-Boiler/Chiller-VAV. System will complete an auto sizing run. and generates an SVG diagram. No apparent error from system disconnects. System has Thermostats and Availability Managers assigned...and while equipment is sized, there is no HVAC energy. Lights and Plugs show up.....but No Fans, No Pumps, 0. Any ideas, b/c I'm buffaloed ? can send file...
Did a Variable for AvailabileManager...its a 2 for all of the hours run. Compared this to another model which IS behaving...its also a 2....I think I've done and redone the availability managers and compared to the 5ZoneVAV E+ example....I'm still confused. Thanks in advance for any ideas....
Maybe your building is really awesome?!
More seriously, do you get unmet hours? Send the file, hard to tell what's causing this...
AvailabilityManager:Scheduled
having a value of 2 is good (see this)do you add cooling and heating setpoints in the space ?
The building isn't anything special - so it better use some energy! There are a ton of unmet hours in the project. I have
Thermostat:Setpoint:DualSetpoint
and that is assigned in each of theZoneControl:Thermostat
....I'll send the file to you @Julien Marrec and will be sure the solution is reported back because I am quite....confused.I guess DualSepoint should be used with plant loop, not air loop