Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
0

Two chilled water loop with different temperature

asked 2017-02-20 01:46:25 -0600

Fish Lee's avatar

Hi, I have a building that has 2 chilled water loop with different loop temperature. Each is cooled by a water-to-water heat pump and providing chilled water to different equipment. Is it possible to have 2 separate chilled water loop with water-to-water heat pumps rejecting heat to the same hot water loop in EnergyPlus?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2017-02-20 08:02:24 -0600

Adam Hilton's avatar

Yes, you can have supply equipment on different loops share the same condenser loop as demand equipment.

edit flag offensive delete link more

Comments

Thanks. As my heat pumps are connected to the same condenser loop and hot water loop but to different chilled water loops, is it still possible to set up 2 central heat pump system and connect them as designed?

Fish Lee's avatar Fish Lee  ( 2017-02-23 20:17:21 -0600 )edit

Build the two chilled water loops and then put two heat exchangers on the demand side of those those loops that are supply components to your condenser water loop.

Adam Hilton's avatar Adam Hilton  ( 2017-02-24 08:25:27 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

Stats

Asked: 2017-02-20 01:46:25 -0600

Seen: 217 times

Last updated: Feb 20 '17