Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

chiller performance curves [closed]

asked 2017-02-12 06:48:11 -0600

Tohagit's avatar

Hello I am trying to model a screw chiller - working in designbuilder. the data I have from the manufacturer is part load, so, according to desighbuilder help file, I generated EIRFPLR using the data i got (using the chiller_performancecurve_coefficients.xls) for EIRFT and CAPFT I used 1 for the first coefficient and 0 for the others. (according to https://www.designbuilder.co.uk/helpv5. ... ht=chiller) the simulation keeps crashing, and the message I get is: (INTEL EIRFPLR is my generated curve)

Severe * GetElecReformEIRChillerInput: Chiller:Electric:ReformulatedEIR="CHILLER 1" * ~~~ ** Invalid Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve Name=INTEL EIRFPLR for Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve Type=LEAVINGCONDENSERWATERTEMPERATURE

Any advices?

edit retag flag offensive reopen merge delete

Closed for the following reason the question is answered, right answer was accepted by Tohagit
close date 2017-02-14 01:23:57.057697

Comments

Did you use °C to generate the curve?

Adam Hilton's avatar Adam Hilton  ( 2017-02-13 08:43:39 -0600 )edit

1 Answer

Sort by » oldest newest most voted
1

answered 2017-02-13 09:42:13 -0600

The last part of the message says the curve type is LeavingCondenserWaterTemperature. For this choice, the valid curve type is a bicubic curve object. What type of curve object did you use?

Curve:Bicubic,
  ReformEIRChiller Carrier 19XR 1259kW/6.26COP/Vanes EIRFPLR,  !- Name
edit flag offensive delete link more

Comments

I fixed the water temperatures - that was the problem.

Tohagit's avatar Tohagit  ( 2017-02-14 01:22:59 -0600 )edit

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2017-02-12 06:48:11 -0600

Seen: 381 times

Last updated: Feb 13 '17