Problems with HVAC System
Hello, at the moment i am writting my Bachelor Thesis about Open studio and Energy Plus. when ever i add an HVAC System to my Modle the Simulation doest work. I dont know how to fix that Problem. I ve read the erro file, but i dont find the Problem Here is the Error file:
Blockquote
Program Version,EnergyPlus-Windows-64 8.1.0.009, YMD=2015.01.05 14:18,IDD_Version 8.1.0.009
************* Beginning Zone Sizing Calculations
** Warning ** GetHTSurfaceData: Surfaces with interface to Ground found but no "Ground Temperatures" were input.
** ~~~ ** Found first in surface=SURFACE 9
** ~~~ ** Defaults, constant throughout the year of (18.0) will be used.
** Warning ** CheckUsedConstructions: There are 7 nominally unused constructions in input.
** ~~~ ** For explicit details on each unused construction, use Output:Diagnostics,DisplayExtraWarnings;
** Warning ** SetUpZoneSizingArrays: Requested Sizing for Zone="THERMAL ZONE 1", Zone has no thermostat (ref: ZoneControl:Thermostat, et al)
** Warning ** SetUpZoneSizingArrays: Requested Sizing for Zone="THERMAL ZONE 2", Zone has no thermostat (ref: ZoneControl:Thermostat, et al)
** Warning ** Calculated design cooling load for zone=THERMAL ZONE 1 is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
** Warning ** Calculated design heating load for zone=THERMAL ZONE 1 is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
** Warning ** Calculated design cooling load for zone=THERMAL ZONE 2 is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
** Warning ** Calculated design heating load for zone=THERMAL ZONE 2 is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
************* Beginning System Sizing Calculations
** Warning ** ManageSizing: Calculated Cooling Design Air Flow Rate for System=PACKAGED ROOFTOP AIR CONDITIONER is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
** Warning ** ManageSizing: Calculated Heating Design Air Flow Rate for System=PACKAGED ROOFTOP AIR CONDITIONER is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
** Severe ** Controller:MechanicalVentilation="CONTROLLER MECHANICAL VENTILATION 2", Design Specification Outdoor Air Object Name blank
** ~~~ ** For Zone="THERMAL ZONE 1".
** ~~~ ** This field either needs to be filled in in this object or Sizing:Zone object.
** ~~~ ** For this run, default values for these fields will be used.
** Severe ** Controller:MechanicalVentilation="CONTROLLER MECHANICAL VENTILATION 2", Design Specification Outdoor Air Object Name blank
** ~~~ ** For Zone="THERMAL ZONE 2".
** ~~~ ** This field either needs to be filled in in this object or Sizing:Zone object.
** ~~~ ** For this run, default values for these fields will be used.
** Severe ** For Controller:OutdoorAir: CONTROLLER OUTDOOR AIR 2
** ~~~ ** maximum outdoor air flow rate (10.0000) < minimum outdoor air flow rate (11.0000)
** ~~~ ** To set the minimum outside air flow rate use the "Design (minimum) outdoor air flow rate" field in the Sizing:System object
** Warning ** Controller:MechanicalVentilation = "CONTROLLER MECHANICAL VENTILATION 2", Zone="THERMAL ZONE 1".
** ~~~ ** No "PEOPLE" object has been specified in the idf for this zone, but the ventilation rate is > 0 in this Controller:MechanicalVentilation Object.
** ~~~ ** Check ventilation rate in Controller:MechanicalVentilation object. Simulation will continue.
** Warning ** Controller:MechanicalVentilation = "CONTROLLER MECHANICAL VENTILATION 2", Zone="THERMAL ZONE 2".
** ~~~ ** No "PEOPLE" object has been specified in the idf for this zone, but the ventilation rate is > 0 in ...
See the previously answered question.