Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Total building equipment and lighting loads in eQUEST

asked 2017-01-30 11:04:37 -0600

dpud12's avatar

updated 2017-01-31 12:02:42 -0600

Hi, is there an easy way to view the total capacity of the installed electrical equipment and/or lighting for a building model in eQUEST? I have searched through the detailed output files but nothing seemed to provide this data.

Thanks in advance for any insights!

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2017-01-31 11:32:12 -0600

Molly Curtz's avatar

updated 2017-01-31 11:34:44 -0600

File menu --> Export file--> Space Loads Report (CSV)

This will report space areas, Lighting Power, and Misc. Equip. Power for all spaces in the model. You can open the CSV file in a spreadsheet and sum the values.

The LPD, EPD and Area are also reported in the SIM output file in the LV-B report. You can copy that into a spreasheet and calculate the total values.

I'm not sure if Misc. Equipment is the extent of what you mean by "installed electrical equipment".

edit flag offensive delete link more

Comments

Thanks! The Space Loads Report CSV is exactly what I was looking for

dpud12's avatar dpud12  ( 2017-01-31 12:22:55 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

2 followers

Stats

Asked: 2017-01-30 11:04:37 -0600

Seen: 918 times

Last updated: Jan 31 '17