Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Unmet hours too high in annual simulation but 0 on design days EnergyPlus

asked 2014-12-25 15:40:22 -0600

updated 2020-03-10 10:49:20 -0600

Hi everyone,

I am using EnergyPlus 8.2 in Ubuntu for performing a series of simulations of a building located in Lima, Peru. Since my intention is to compare a reference and a proposed model (i.e. ASHRAE 90.1), there are two models: one with almost everything autosized, and the other with nearly everything predefined (except those values not clearly specified by the HVAC engineer).

Anyways, both models run Sizing:Plant and Sizing:Zone calculations, and there seem to be no important errors in the *.err file (only a few convergence ones... the system corresponds to System 8 on Appendix G: VAV PIU with Reheat).

When simulating the sizing periods (i.e. winter and summer design days) every conditioned zone's temperature lies between setpoints (21 and 24 °C); so I assume Sizing is being done correctly. However, when simulating the whole year, the results show about 3000 unmet hours, using a tolerance of 0.55°C. This happens with both the proposed and reference building.

I, honestly, do not know what to check anymore... any suggestions?

THANKS VERY MUCH IN ADVANCE! HAPPY HOLIDAYS!

edit retag flag offensive close merge delete

3 Answers

Sort by » oldest newest most voted
4

answered 2014-12-26 18:53:05 -0600

Archmage's avatar

It is difficult to pinpoint an answer given this much information, but here are some possible reasons to explore:

  1. The summer design day is of the type that has high drybulb with mean coincidenct wetbulb, but often cooling coil loads are larger for high wetbulb with mean coincident drybulb. The program will select the design day with the highest sensible zone load, so sometimes you have to remove the DB->MWB day from input to force it to use the WB->MDB day. This often comes up for dry climates, which I would think is the case for Lima.

  2. The schedules that are important for controls are setup one way for the design days, but then differ for the regular types of days so that the system is not really running properly when changing from design days to annual run.

  3. Sun angles for a mid-summer are high, but shoulder seasons have lower sun angles which actually lead to higher gains in the space, regardless of outdoor temperatures. Add some additional design days that cover shoulder seasons, even covering all twelve months.

As always, you'll want to study detailed timeseries results for air system nodes to diagnose what is really going on during those hours not met.

edit flag offensive delete link more
2

answered 2014-12-30 14:50:51 -0600

Joe Huang's avatar

3000 unmet hours is clearly too many, because that 's almost 35% of the entire year, so obviously something is seriously wrong here. I can't tell from your description the difference between the two models - are they the same building, only one with autosized equipment and the other with capacities specified by the engineer, or is one a reference building w/autosized equipment and the other the candidate building with predefined equipment capacities ? If the former, then you can just compare the autosized capacities to the predefined ones and see how much is the undersizing. If the latter, then you can't compare the capacities (because the building loads are different), but you can bump up the autosized capacities and watch how the number of unmet hours decrease. I'm not certain, but I believe that EnergyPlus allows input for a Sizing Factor to make it easy to do this.

However, before doing any such exploration, make sure that your design calculations are not faulty - (1) Is the DDY file for the same location and how do the design conditions compare to the maxima on the weather file, (2) is the right month being used to calculate the clear sky radiation? (it should be either January or February for Lima, not July or August as typically used for North America).

edit flag offensive delete link more
1

answered 2015-01-03 16:08:43 -0600

Thanks for the Advise, everyone. I found the main problem: Ventilation values for sizing and simulation were different. I guess the temperatures being correctly in the sizing periods was just "luck".

Now, I see that the unmethours is still high... That, I assume, is because the Design Days are not the "actual peaks".

THANKS

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2014-12-25 15:40:22 -0600

Seen: 429 times

Last updated: Jan 03 '15