Control of AirTerminal:SingleDuct:VAV:Reheat
I assigned a typical VAV system with reheat but there are many heating unmet hours in the core area. After I did further check for node temp as well as air cfm and found:
1) the air cfm is almost fixed all the time, like CAV 2) although I set the sizing air inlet/outlet temp for heating coil in reheat is 13C/35C. However, the heating coil can only heat the air to around 18C, even though the heating is not enough at that time. Therefore, it came out the unmet hours.
Anyone had same problem? Don't know what's wrong with the setup.
Here is the link for my sample model, which is a 5-floor small building with typical 5 zone in each floor: link
Can you check node temperatures (and unmet hours) once you replace "Normal" Damper Heating Action with "Reverse" in all AirTerminal:SingleDuct:VAV:Reheat objects?
@Ivan Korolija, thanks for your reply. Actually I do check this. In this sample model, if I changed "Normal" to "Reverse", the unmet hours did go. Also, the hot water coil temp increase a little bit. But air flow rate is still the same which I thought should be different. And this action did not apply to other models. I mean, for this model, "Reverse" will remove unmet hours. However, for other models. it removed unmet hours but created more unmet hours in other zones. So I was wondering if this is the correct action I should take