Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

OS - Heat a Space but do not Include Energy Needed into Model?

asked 2016-12-14 18:52:39 -0500

cnutt's avatar

updated 2017-04-27 13:53:49 -0500

I have a multifamily building built on a podium over retail. I am not modelling the retail energy use but I would like to make the retail space conditioned so as not to negatively affect the HVAC loads in the units touching the retail. How would I go about doing this?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2016-12-15 13:36:01 -0500

updated 2016-12-15 13:44:40 -0500

Set the retail thermal zones to be conditioned by ideal air loads, and then ignore the district heating and district cooling energy use in your model outputs. This is assuming you aren't using ideal loads for other zones in your model and that you aren't using a district source for other heating/cooling in your building. (EDIT): Another option is to set the surfaces between the retail and residential spaces as adiabatic

edit flag offensive delete link more

Comments

I would recommend setting the surfaces between the retail and residential spaces as adiabatic as mentioned above. This is a much easier solution.

TaylorRoberts's avatar TaylorRoberts  ( 2016-12-15 16:40:26 -0500 )edit

If you use adiabatic boundary just make sure you hard assign a construction, since it won't inherit from construction set. Some scripts and measures that assign adiabatic boundary condition may do this for you.

David Goldwasser's avatar David Goldwasser  ( 2016-12-16 13:16:54 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2016-12-14 18:52:39 -0500

Seen: 113 times

Last updated: Dec 15 '16