Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

A problem about model building in energyplus

asked 2016-12-14 11:00:26 -0500

gaofeng's avatar

updated 2017-01-27 14:52:38 -0500

When I run the simulation in E+, there is always a warning as follows:

Warning ** GetSurfaceData: InterZone Surface Areas do not match as expected and might not satisfy conservation of energy:
   **   ~~~   **   Area=306.2, Multipliers=1, Total Area=306.2 in Surface=SURFACE 12 Zone=THERMAL ZONE 1
   **   ~~~   **   Area=306.2, Multipliers=3, Total Area=918.7 in Surface=SURFACE 53 Zone=THERMAL ZONE 2

I want to know how I can fix this problem?

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
2

answered 2016-12-14 11:56:59 -0500

Are you using a zone multiplier one of of two adjacent thermal zones? If so, you may consider switching those surfaces to adiabatic. That is what is often done for the floor/ceiling boundary where there is a mid floor with zone multipliers greater than 1 and top and bottom floor multipliers that are 1.

If you see this warning and the area difference in area is very small in non-multiplier scenario then it could probably be ignored.

edit flag offensive delete link more

Comments

Thank you for your help, I will change it and check the result. But I always have another question for thermal zone. That is whether I can set two zones which locate in different storeys into a same thermal, or I can just set the zone in same storey to the same thermal zones.

gaofeng's avatar gaofeng  ( 2016-12-15 03:25:52 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2016-12-14 11:00:26 -0500

Seen: 423 times

Last updated: Jan 27 '17