Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Central heating loop for a building with several thermal zones

asked 2016-11-29 17:56:57 -0500

Reid's avatar

updated 2016-12-01 13:28:11 -0500

Hello.

I am trying to create for educational reasons, a central heating loop with a hot water boiler, in a building with more than ten thermal zones, by using the openstudio program.

I am new in energy modeling so i am faced with some difficulties. First of all i would like to ask if there are any radiators in the openstudio library? Moreover, how could i be able to import the thermal zones into the plant loop? Is it right, in order to control the radiators indepentently , to put o scheduled HW Temp before each radiator?

Thank you in advance.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2016-11-30 07:12:19 -0500

Matt Koch's avatar

1) Under the HVAC tab, when you select Library on the right side of the screen while designing an air loop, you might pick from Coil Heating Electric -> Unit Heater Elec Htg Coil or Coil Heating Gas -> Unit Heater Gas Htg Coil or Coil Heating Water -> HW Htg Coil/Unit Vent Heat Coil. I think that should get you started on the radiators, though I think based on your question, you'll pick a Coil Heating Water item.

2) You will likely generate a plant loop to generate hot water with a boiler and an air loop with the Coil Heating Water item. In the air loop, when you select My Model rather than Library on the right side of the screen, you will see Thermal Zones listed further down. From there you can drag a thermal zone into the air loop and place it left of the Coil Heating Water item.

3) The plant loop must have a Set Point Manager on the outlet side of the supply half. This will set the hot water temperature to, say, 180 oF - there is only one of these. Then, under the Thermal Zones tab, each thermal zone must have a Heating Thermostat Schedule. It is in those schedules where you tell OpenStudio what each zone temperature is supposed to be (zone set point as opposed to loop set point). OpenStudio then will simply vary the hot water flow rate through the Coil Heating Water item to maintain the zone temperature.

edit flag offensive delete link more

Comments

Hello! I am also new in energy modeling, and I also create a heating system. Following your advice, I have a question: how to place the thermal zone to the left of the coil? Because the coil is in the supply area, and thermal zones can only be inserted into the demand area. I would be very grateful if you could show a screenshot of how such a system looks. Thank you in advance!

Chizh's avatar Chizh  ( 2018-12-21 10:30:48 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

Stats

Asked: 2016-11-29 17:56:57 -0500

Seen: 651 times

Last updated: Nov 30 '16