How to use Chiller:Electric:ReformulatedEIR in openstudio
I have manufacturer's ReformulatedEIR curves. How can I get Chiller:Electric:ReformulatedEIR in my openstudio plant loop?
First time here? Check out the Help page!
I have manufacturer's ReformulatedEIR curves. How can I get Chiller:Electric:ReformulatedEIR in my openstudio plant loop?
You'll have to use an EnergyPlus Measure to add this, as this object is not supported by OpenStudio.
I would:
If you set up the chiller and curve objects in their own idf, you can use the inject idf objects measure to put those objects into your model. Then, if you don't want to figure out how to connect them via measure, you'd have to open up the out.idf and hook up the chiller manually.
I have an EnergyPlus Measure that does this for a Chiller:ConstantCOP that could be adapted. In addition to updating the Branch that the Chiller:Electric:EIR is on, the EP measure will also need to update the PlantEquipmentList.
No, editing the OSM directly is a dangerous operation that can corrupt your model if you're not careful and in this case OpenStudio doesn't know how to translate it to EnergyPlus (not currently in the API). Andrew's or Eric's suggestions are the only ways to do this currently.