Air Loop Free Cooling

asked 2016-09-23 04:13:36 -0600

Diego's avatar

updated 2016-09-23 11:22:20 -0600

Hi, i'm simulating an Air-Water system with OpenStudio. Into the central air handling unit there is only one coil, for heating in winter and cooling in summer. The problem is that air temperature of all zones go down when change the season (from heating to cooling or from cooling to heating). Is there a way to stop cooling coil when outdoor air is enough cold for cooling (free cooling)?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2016-09-27 13:52:24 -0600

Sounds like you're talking about the Economizer settings.

Here's how you access these in the GUI: image description

edit flag offensive delete link more