Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

Air Loop Free Cooling

asked 2016-09-23 04:13:36 -0500

Diego's avatar

updated 2016-09-23 11:22:20 -0500

Hi, i'm simulating an Air-Water system with OpenStudio. Into the central air handling unit there is only one coil, for heating in winter and cooling in summer. The problem is that air temperature of all zones go down when change the season (from heating to cooling or from cooling to heating). Is there a way to stop cooling coil when outdoor air is enough cold for cooling (free cooling)?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2016-09-27 13:52:24 -0500

Sounds like you're talking about the Economizer settings.

Here's how you access these in the GUI: image description

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2016-09-23 04:13:36 -0500

Seen: 637 times

Last updated: Sep 27 '16