Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
4

Modelling fenestration to Appendix G - LEED

asked 2016-08-20 11:41:28 -0600

I'm working on a baseline model to meet the LEED certification ASHRAE Standard 90.1 in OpenStudio 1.11 .

In order to set up the U-Factor to exterior fenestration to meet the 90.1-2007 Region 1A, I would need to reach 6.81 W/m².K.

In the first submission to USGBC, I had used a component from OpenStudio Office Library: “ASHRAE 90.1-2007 ExtWindow Metal ClimateZone 1”, that uses Simple Glazing System Window Materials. However, the U-Factor result in the report Envelope Summary: Exterior Fenestration, after considering the film, was 5.827 W/m².K, different from the said 6.81 W/m².K.

In the review, the USGBC asked me to correct the U-Factor to the values in the Standard .

So, I tryed to use a component from BCL: “90.1-2007 Nonres 1A Window Metal framing all other”, that uses another method to model the glass. In this case, the Glass U-Factor in Envelope Summary is 6.42 W/m².K, not meeting the requirements again.

I was beggining to correct this manually, but as explained in this question, it is impossible to get this U-Factor only by modeling the glass, because of the convection thermal resistance from the films. I imagine that I need to model the Frames manually to do as requested, but I’m not sure if this is the real problem and how I could fix it.

For the Proposed Model, I have similar problems, but with U-Factor 7.1 W/m².K from Table A8.2 from ASHRAE 90.1 - 2007.

How can I model windows to meet these requirements and demonstrate this in the reports to the USGBC? Which is the best current way that have been used to model this in EnergyPlus?

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
4

answered 2016-08-31 10:51:10 -0600

You can fix the window u-value firm if you use the object in EnergyPlus called: "WindowMaterial:SimpleGlazingSystem" This object asks for a u-factor, solar heat gain coefficient and visible transmittance. It assumes that the numbers you are putting in are for the whole assembly (glazing and frame). This is counted as a material and so needs to be added to a construction. However no film will be taken into account and you will get the identical u-value you put in here, in the output reports.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

2 followers

Stats

Asked: 2016-08-20 11:41:28 -0600

Seen: 958 times

Last updated: Aug 31 '16