Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

ASHRAE 90.1-2007 App G PRM G3.1.2.4

asked 2016-08-03 10:57:05 -0500

Sean King's avatar

updated 2016-08-03 11:50:46 -0500

As I have searched web and try to understand the 90.1 clause G3.1.2.4, the system needs to use night cycle and keep outdoor air flow rate to zero. I therefore just have a simple question, if above understanding is right, how re-circulation (no outdoor air) alone to meet the cooling/heating loads from zones during unoccupied hours? Do coils work as well during night cycle? Thank you very much in advance for any reply.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2016-08-03 15:41:17 -0500

During unoccupied hours the outdoor air damper should close and then the unit should cycle on and off to meet the setback setpoint. To meet the setpoint, the heating and cooling coils should also turn on and off.

If you are using EnergyPlus/OpenStudio I can show you exactly how to do this, if you are using another program tell everyone and I am sure someone will know.

edit flag offensive delete link more

Comments

Hi Taylor, Thank you very much for your reply. Yes, I am using EnergyPlus, could you please demonstrate me what to do? Thanks.

Sean King's avatar Sean King  ( 2016-08-04 02:35:54 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2016-08-03 10:57:05 -0500

Seen: 189 times

Last updated: Aug 03 '16