Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
5

Zone multipliers and hardsized capacities in EnergyPlus

asked 2016-07-18 09:19:51 -0500

updated 2016-07-18 09:20:07 -0500

I'm using zone multipliers. Say zone A and B are exactly the same. Zone A is conditioned with a 10,000 BTU cooling system.

If I model Zone A only and apply a zone multiplier of two, what will I need to input as far as Nominal Cooling Capacity for my cooling system? 10,000 BTU or 20,000 BTU?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
5

answered 2016-07-18 09:39:06 -0500

updated 2016-07-18 09:40:12 -0500

I'd say 20,000 BTU. From the I/O: "It takes the calculated load for the zone and multiplies it, sending the multiplied load to the attached HVAC system. The HVAC system size is specified to meet the entire multiplied zone load and will report the amount of the load met in the Zone Air System Sensible Heating or Cooling Energy/Rate output variable.

edit flag offensive delete link more

Comments

Agreed. This has been my experience with hard-sized models of proposed designs.

MatthewSteen's avatar MatthewSteen  ( 2016-07-18 09:43:42 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2016-07-18 09:19:51 -0500

Seen: 339 times

Last updated: Jul 18 '16