free cooling with geotabs

asked 2016-06-22 04:53:36 -0600

updated 2016-06-22 10:25:32 -0600

Hi,

I'm modeling a geotab system for a building. The system has a borehole field connected to a heat pump for heating. As for cooling, I use the water temperature coming from the ground 12-13°C to do some free cooling.

On DesignBuilder, we cannot connect directly the borehole fields to the secondary loop, but we need to set a cooling heat pump with its characteristics. Do you know how to model this passive cooling by eliminating the cooling capacity of the HP? I hope I was clear.

Many Thanks,

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
1

answered 2018-06-13 10:59:36 -0600

t0b1.de's avatar

you can connect the borehole field to the demand site by using a fluid heat exchanger. (condenser loop slippter/mixer to CHW Loop supply slitter/mixer)