Warning - Calculated Relative Humidity out of range

asked 10 years ago

nfonner's avatar

updated 10 years ago

I am constantly seeing this warning:

* Warning * Calculated Relative Humidity out of range (PsyRhFnTdbWPb) * ~~~ * Routine=CalcMultiSpeedDXCoil:lowspeedoutlet, Environment=RUN PERIOD 1, at Simulation time=04/12 13:00 - 13:10 * ~~~ * Dry-Bulb= 3.21 Humidity Ratio= 4.897E-003 Calculated Relative Humidity [%]= 101.01 * ~~~ * Relative Humidity being reset to 100.0%


Any thoughts on if this is something I can ignore?

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
4

answered 10 years ago

Hard to make a blanket comment without knowing more about what's happening in the model. A leaving dry-bulb temp of 3.2C (37.8F) is rather cold off a DX coil, so the airflow to capacity ratio for this coil may be too low.

Preview: (hide)
link

Comments

1

Looks like increasing the Constant Minimum Airflow Fraction above the minimum ventilation rate was part of the issue. The warning persists, but was much less "severe" at a DB to 9.48 C for that same model.

Thanks Michael.

nfonner's avatar nfonner  ( 10 years ago )