Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Is it legal to split one room into several zones in EnergyPlus?

asked 2016-06-02 08:11:51 -0600

Verla gravatar image

updated 2016-06-02 10:15:22 -0600

Urado gravatar image

The model in EnergyPlus is actually a room, but I want to consider the different locations of supply air. Is it legal to cut the room into several parts? If so I am planning to use the AirFlow Network model. Or any better solutions?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2016-06-02 10:06:58 -0600

Urado gravatar image

Following the ISO 13790, it is not:

In particular you have not to dived a space in more thermal zone if:

  1. Set-point temperatures for heating/cooling of the spaces differ by no more than 4 K;

  2. The spaces is serviced by the same heating systeme (if any) and the same cooling system (if any);

  3. At least 80% of the floor area are serviced by the same ventilation system;

  4. The ammount of ventilation (in cubic metre per square metre of floor area per second) differs by not more than a factor of 4 within 80% of the floor area.

edit flag offensive delete link more

Comments

Thank you, Urado. I will check the model later.

Verla gravatar imageVerla ( 2016-06-03 03:43:34 -0600 )edit