I'm having difficulties implementing a gas-heated system in the HVAC system part of Open studio. I don't have any experience regarding HVAC system so I would like to ask your help.

What I want is a system consisting of a boiler, delivering heated water to a radiator/CV system in my building and the taps. I implemented the taps, but for some reason the radiator is not taking any power at all. The main consumer of energy is just the pump.

The radiator I'm using is called 'Zone HVAC Baseboard Rad Conv Water' and is connected to the demand part of the loop, just like the taps. image description

edit retag flag offensive close merge delete

Comments

You should now be able to upload an image given that you have 10 karma points. Please do (and include a screenshot of your hot water plant loop from OS too).

Also remember in the future to always tag your question with the software you are using if that's relevant (openstudio here)

Julien Marrec's avatar Julien Marrec  ( 2016-05-30 02:30:41 -0600 )edit

Thank you, I've added a screenshot of the system.

PolBogus's avatar PolBogus  ( 2016-05-30 02:50:28 -0600 )edit

1 Answer

Sort by ยป oldest newest most voted
2

answered 2016-05-31 17:32:35 -0600

NickC's avatar

How confident are you in the plant loop settings? I'm not familiar with 'Zone HVAC Baseboard Rad Conv Water', but many plant operation/consumption issues can be traced back to default plant loop settings. https://unmethours.com/question/17388...

Also, many modelers recommend adding extra adiabatic piping to plant loops.
https://unmethours.com/question/11297...

edit flag offensive delete link more

Comments

OpenStudio will add the adiabatic piping to your plant loop. If you add a demand side bypass it adds (or use to add?) an extra one too.

Julien Marrec's avatar Julien Marrec  ( 2016-06-01 00:40:27 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2016-05-29 03:54:00 -0600

Seen: 473 times

Last updated: May 31 '16