Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

Thermostat Tolerance in AvailabilityManager:NightCycle

asked 2016-05-26 03:28:17 -0600

Urado's avatar

I don't understand the thermostat tolerance :

The zone temperature must exceed the cooling set point or fall below the heating set point by 1/2 the Thermostat Tolerance in order for the availability manager to signal that the system should turn on.

I want the heating to turn on at night if the temperature falls below 14 °C. I have my heating set point to 16 °C, my tolerance thermostat to 4 °C and my cycling run time to 1600s. So I expected my system to turn on at 16-4*1/2 = 14 °C and to stay on during 1600s. However it is not the behavior I observed: T.PNG

I have only two zones controlled with this NightCycle: image description

Any thoughts on what happens ?

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
1

answered 2016-05-26 08:49:26 -0600

Chandan Sharma's avatar

Once the zone/s temperature falls below 14 C, night cycle turns on the fan which remains on for 1600 s (26.67 minutes). After 1600 s, fan is off for entire zone time step(15 min if Timestep input is 4 and 10 min if Timestep input is 6 etc.). After that night cycle again turns on the fan which remains on for 1600 s and the cycle continues. This is the behavior above plot is showing. Reporting times series data at detailed or timestep frequency will make it easier to see what is happening.

edit flag offensive delete link more

Comments

The behavior you described is what I expect but not what I observe. The plot I showed already uses timestep frequency (10 min) so why my system turns on above 14 °C ?. Here it's more like 14.8°C and it's not even regular.

I would have understood if it turned on a little below 14 °C (due to the 10 min timestep)...

Urado's avatar Urado  ( 2016-05-26 09:23:01 -0600 )edit
1

Is output variable Availability Manager Night Cycle Control Status at detailed frequency showing expected control status? If not can you attach spreadsheet with zone temperatures, and above output variable reported at detailed frequency.

Chandan Sharma's avatar Chandan Sharma  ( 2016-05-26 09:44:11 -0600 )edit

Thanks a lot, Timestep (used for the plot) was not enough to see the temperature fall below 14°C ! With Detailed I can observe it:

  • 02/12 04:10:00 14.0875908
  • 02/12 04:12:30 13.82292834
  • 02/12 04:15:00 13.81977706
  • 02/12 04:17:30 14.32698974
  • 02/12 04:20:00 14.98434769
Urado's avatar Urado  ( 2016-05-26 10:32:27 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2016-05-26 03:28:17 -0600

Seen: 426 times

Last updated: May 26 '16