Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
4

Open Studio: Modelling a mechanical ventilation system (no coils) and a baseboard:radiantconvective:water system for 2 zones

asked 2014-12-05 04:14:24 -0600

KDE's avatar

updated 2014-12-05 04:19:03 -0600

Hello,

I want to model two zones which are connected on one mechanical ventilation system without any coils. So pure for ventilation purposes. These 2 zones must be heated by radiators ( baseboard:radiantconvective:water system), which are connected on one hot water plant loop (so on 1 boiler).

In Open Studio, tab 'Thermal zones', I think I have it implemented on the right way, but I don't know how to do it in the tab 'HVAC system' (I can't add these baseboards in this tab, only in the tab 'thermal zones').

Can you help me?

I would like to give you my OSM file to have a look but don't know how on this platform.

Thanks in advance!

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
8

answered 2014-12-05 08:53:08 -0600

Your baseboard heaters should look something like this when viewed in the thermal zones tab.

image description

Next switch over to the hvac tab and add a hot water plant to supply the baseboard heater. There is no template for a generic hot water plant, so you need to add a blank plant loop and populate it with a pump, a boiler, and a scheduled setpoint manager on the supply outlet node. It should look something like this when you are done.

image description image description

Now switch back over to the zones tab and add the baseboards to your new plant.

image description

If you go back to hvac tab you should now see the baseboard heaters attached to the plant.

image description

Now add an empty air loop system to provide the ventilation.

image description

Add an air loop hvac outdoor air system, a fan, an air terminal single duct uncontrolled. (or variable speed fan and vav terminal if that is the case) It should look like this.

image description

Now click on either the splitter or the mixer and attach the zones.

image description image description

edit flag offensive delete link more

Comments

The description is very instructive. I will admit though that I would find it more intuitive to have the coil water baseboard heating added to the library as an object that could be added to a plant loop.
https://www.dropbox.com/s/ficnlcquc9e...

MattStewart's avatar MattStewart  ( 2015-03-22 04:09:49 -0600 )edit

As a new user, the images really helped. Thanks

I'll add a couple more details that I needed when switching from ideal loads to hydronic:

  1. Moving from ideal loads to this loop, you'll need to add a design day weather file (ddy).
  2. For the setpoint manager on the supply side, you set "control variable" to "temperature".
  3. In the zone section, as with ideal air loads, you need to have a "heating thermostat schedule" and a "cooling thermostat schedule", even if you don't have any cooling equipment.
  4. Under simulation settings, turn on zone/plant sizing calculations if using auto-sizin
alex j's avatar alex j  ( 2018-09-13 16:23:19 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2014-12-05 04:14:24 -0600

Seen: 2,045 times

Last updated: Dec 05 '14