Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Loop Design Temperature Difference

asked 2016-05-14 11:23:38 -0600

Carlos Vazquez's avatar

I can´t find within openstudio where to specify the loop design temperature difference for sizing plants, either for a chilled water or cooling tower loop. The autosizing reports that I am getting are assuming a default of 19.80 degrees Fahrenheit to autosize the pump flow rate. After exporting an idf file I am able to specify plant sizing parameters within the energyplus idf editor. Is this something that is not available within the openstudio application? Or is there a way to specify it within openstudio?

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
2

answered 2016-05-15 08:26:58 -0600

updated 2016-05-15 08:28:18 -0600

The Plant:Loop and Sizing:Plant objects can be edited by clicking on the dashed line separating the Supply Equipment and Demand Equipment of the PlantLoop.

edit flag offensive delete link more

Comments

I just verified it. That´s correct. Thank you your answer Matthew! I was not aware of that.

Carlos Vazquez's avatar Carlos Vazquez  ( 2016-05-16 08:08:52 -0600 )edit
1

problem solved then, please mark the answer as accepted by clicking on the check mark next to the post (to the left)

Julien Marrec's avatar Julien Marrec  ( 2016-05-16 09:33:28 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2016-05-14 11:23:38 -0600

Seen: 1,748 times

Last updated: May 15 '16