Differences between VAV:Reheat and VAV:HeatAndCool:Reheat
I'm searching for further clarification on the differences between VAV:Reheat
and VAV:HeatAndCool:Reheat
. The distinctions between the two for me became muddled after reading through this question.
In the input output reference under VAV:HeatAndCool:Reheat
the airflow rate of the VAV:Reheat
object is said to be...
"...reduced to the minimum value (max air flow rate x zone minimum air flow fraction) when zone heating is required."
But there are parameters in the VAV:Reheat
object that in my eyes don't agree with that statement such as Maximum Flow Fraction During Reheat. This field is a fraction that...
"...is multiplied by the Maximum Air Flow Rate to determine the maximum volume flow rate (m3/s) allowed during reheat operation..."
This, to me, indicates that the air flow is indeed modulated during heating for VAV:Reheat
.
If what is said about VAV:Reheat
under VAV:HeatAndCool:Reheat
is true shouldn't the air flow for VAV:Reheat
during heating operation simply be whatever is defined in the object by the Zone Minimum Air Flow Method?
Documentation verbiage aside, here's how I would expect the two objects to behave. VAV:Reheat
modulates the reheat valve to 100% first, then increases air flow whereas VAV:HeatAndCool:Reheat
increases the air flow to maximum first, then modulates the reheat valve to 100%. Is this correct? Am I just doing a poor job of reading the documentation?