4

Modeling a building with heavy electrical component gains [closed]

asked 2016-04-20 05:05:22 -0600

FSilenzi's avatar

updated 2016-04-29 09:20:54 -0600

I need to model a building (31 x 18 x 4 m) with no windows. The building is made of polyurethanic panels that should assure the insulation during hot months. Inside the building I have a very high electric load (50MW) that can dissipate up to 5% of this power as thermal contribution. Obviously this electrical load is not working at full capacity all the time. How can I simulate this kind of load? I have tryed with both "electric equipment" and "other equipment" loads but the simulation stops with this error:

Temperature (high) out of bounds (209.38] for zone="THERMAL ZONE 1", for surface="SURFACE 5" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:20 - 12:30 * ~~~ * Zone="THERMAL ZONE 1", Diagnostic Details: * ~~~ * ...Internal Heat Gain [4480.287] W/m2 * ~~~ * ...Infiltration/Ventilation [0.000] m3/s * ~~~ * ...Mixing/Cross Mixing [0.000] m3/s * ~~~ * ...Zone is part of HVAC controlled system.

I assumed that the temeprature rises too much also because I have not well defined the materials, infact I have simulated a hot day (15 august) and the temperature inside the building with NO gains in it rises up to 34 °C. This should not happen since the panels are supposed to insulate the building.

I have tryed to turn on ideal loads to have an idea of the size of the HVAC system that have to be installed there.

For the polyurethane panels I have defined a new material with these specifics:

image description

The load schedule is a fractional set to be 0 except for an hour a day, in which I have the maximum thermal dispersion from the electical load.

edit: I have set the radiant fraction to 0 and rerun the simulation that unfortunately stops with the following error:

* Severe * Temperature (high) out of bounds (212.96] for zone="THERMAL ZONE 1", for surface="SURFACE 1" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41 * ~~~ * Zone="THERMAL ZONE 1", Diagnostic Details: * ~~~ * ...Internal Heat Gain [448.029] W/m2 * ~~~ * ...Infiltration/Ventilation [0.000] m3/s * ~~~ * ...Mixing/Cross Mixing [0.000] m3/s * ~~~ * ...Zone is part of HVAC controlled system.

* Severe * Temperature (high) out of bounds (221.06] for zone="THERMAL ZONE 1", for surface="SURFACE 5" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41

* Severe * Temperature (low) out of bounds [-127.12] for zone="THERMAL ZONE 1", for surface="SURFACE 1" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41

* Severe * Temperature (low) out of bounds [-126.17] for zone="THERMAL ZONE 1", for surface="SURFACE 5" * ~~~ * During Warmup & Sizing, Environment=BIRMINGHAM ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 12:40 - 12:41

* Severe * Temperature (high) out of bounds (221.80] for zone="THERMAL ZONE 1", for surface="SURFACE 2 ... (more)

edit retag flag offensive reopen merge delete

Closed for the following reason question is not relevant or outdated by FSilenzi
close date 2016-06-10 02:39:46.996537

Comments

Hmm, the temps look worse. Try setting the fraction lost to 1 and see if that works. 50MW of electric equipment is a lot!

MatthewSteen's avatar MatthewSteen  ( 2016-04-29 11:22:41 -0600 )edit

They are indeed a lot, but it is a high power electric conversion building that needs to be cooled out, the equipment is 50MW in size and dissipates up to 5% when it is working at full power. Howerver, setting the fraction lost to 1 allows the simulation to run, but it turns out that there is no need for cooling, even if the Zone air temperature reported in result viewer rises up to 40 °C, and the thermostat is set to 30° for cooling.

FSilenzi's avatar FSilenzi  ( 2016-05-02 02:08:51 -0600 )edit

2 Answers

Sort by » oldest newest most voted
3

answered 2016-04-23 14:38:47 -0600

Add this to your input file:

OutputDiagnostics,ReportDuringWarmup; 

OutputVariable,*Surface Inside Face Temperature.detailed;

Then look at the simulation results to see what is happening.

What did you use for "Fraction Radiant" when you tried using the ElectricEquipment object?

edit flag offensive delete link more

Comments

I have used 30% for fraction radiant, when using both other equipment and electrical equipment. What about the space heating during summer even if the walls are supposed to be insulating?

FSilenzi's avatar FSilenzi  ( 2016-04-27 01:58:59 -0600 )edit

Set the radiant fraction to 0 to see if the simulation runs. If it does, raise the fraction gradually while watching inside surface temperatures to see the radiant impact.

rraustad's avatar rraustad  ( 2016-04-28 10:18:39 -0600 )edit
1

answered 2016-04-29 07:56:50 -0600

When I've encountered this error I've been able to fix it by increasing the Fraction Lost. If only 5% the electric equipment load is converted to waste heat, then I would set the fraction lost to 0.95 and the remaining heat fractions to 0, which will result in a convective fraction of 0.05 to the zone.

edit flag offensive delete link more